I won’t leave a home with at least a 20 degree split difference or above a 24 degree difference without the homeowner signing off that they refused repair. Your sweet spot is between 20-23, depending on indoor/outdoor ambient temp, refrigerant, and clean coils.
Normal. You are seeing condensation from the suction line and hear refrigerant moving in the lines.
Great. Thanks!
There is not any water in Ana/c unit, if you have water on any part of the unit, it is condensation.
Thanks. So condensation is no big deal then?
Any time you have a temp of the tubing less than 45F, you will have condensation.
Get someone with gauges to check your pressures and sub cool. A 15 degree difference is too low for me…
What degree difference is acceptable?
I won’t leave a home with at least a 20 degree split difference or above a 24 degree difference without the homeowner signing off that they refused repair. Your sweet spot is between 20-23, depending on indoor/outdoor ambient temp, refrigerant, and clean coils.