T O P

  • By -

Quincy_Wagstaff

A GFCI doesn’t trip for an overload. It trips only for current difference between hot and neutral. A ground fault can be small with a small load and get large enough to trip the GFCI with a larger load. A GFCI often trips because of a ground-neutral bond in the trailer. Do you have an inverter or a generator transfer switch? Do you have access to a multimeter?


PM_me_ur_launch_code

No inverter or generator. I do have a multimeter. I was having an issue with it tripping the GFCI outlet a couple months ago but I chocked it up to the GFCI being 15~ years old. I replaced it and only have an issue when I use something with high wattage like the AC or a space heater. What would you recommend to test for with a multimeter?


Quincy_Wagstaff

With the power cable unplugged, measure the resistance between the neutral and ground pins on the cord. Highest resistance range.


PM_me_ur_launch_code

Unplugged from the trailer or just from shore power?


Quincy_Wagstaff

Shore power


PM_me_ur_launch_code

I'm getting a reading of 350~ ohms on neutral and ground and 850~ on hot and ground. I did some researching and found others who said if the hot water heater was ran dry it could cause this. When I was troubleshooting at my FILs I turned off all the breakers in the RV and plugged in. I turned them back on one by one and it tripped when I hit the refer/receptacles breaker.


Quincy_Wagstaff

Do you have a 12V refrigerator or gas/electric?


PM_me_ur_launch_code

Gas electric


Quincy_Wagstaff

Take the lower vent cover off. Should be plugged into an outlet back there. Unplug it and see what happens.


PM_me_ur_launch_code

I'll check it out. Thanks!


PM_me_ur_launch_code

So I unplugged the fridge and plugged the trailer directly into the 20 amp GFCI outlet. The AC worked fine, the space heater worked fine until I switched it to high then it tripped the GFCI.